FortiSwitch
FortiSwitch: secure, simple and scalable Ethernet solutions
ehamud
Staff
Staff
Article Id 276625

 

Description This article describes how to avoid Error Type 6 when PoE ports are not coming up.
Scope FortiSwitch.
Solution

Sometimes FortiSwitch shows a special Error Type 6 and 'Startup Failure' error. It means that more than 400mA are under some specific Access points. When this happens, the FortiAP loses connection with its Controller.

 

Let´s diagnose one port, port4 shows this abnormal status:

 

FortiSwitch1 # diag switch poe status port4
Port(4) Power:0.00W, Power-Status code: 5(Fault)
Power-Up Mode: Normal Mode
Power Fault: Error Type 6 (Startup Failure)
Remote Power Device Type: IEEE802.3AT PD
Power Class: 4
Defined Max Power: 30.0W, Priority: High.
Voltage: 0.00V
Current: 0mA
Temperature: 31.25 Centigrade

 

In order to fix it,  use the following commands in this order.


Go to the port or ports with the issue and execute:

 

config switch physical-port
    edit portX
        set poe-port-mode IEEE802_3AF
    end
end

 

If it does not help, try this command:

 

config switch physical-port
    edit portX
        set poe-port-mode IEEE802_3AT
    end
end

 

Also, it is important to note that when it is necessary to connect two PoE ports, it is mandatory to disable the PoE function on both ports before the rj45 connection occurs using this command. If not, it will probably get the same error type 6:

 

config switch physical-port
    edit portX

        set poe-status disable

    end

end

 

For more information, check this related document:
Configuring power over Ethernet on a port

 

 One example of healthy behavior is the following diagnosis:

 

diagnose switch poe status port6

Port(6) Power:4.20W, Power-Status: Delivering Power

Power-Up Mode: Normal Mode

Remote Power Device Type: IEEE802.3AT PD

Power Class: 4

Defined Max Power: 30.0W, Priority:3

Voltage: 54.00V

Current: 71mA

 