kgodfrey
Staff
Staff
Article Id 197277
Description

This article provides an example of a Shelf Manager log entry, and explains how to find out more information through basic Shelf Manager commands.  It assumes a working knowledge of the 5000 chassis Shelf Manager functionality and software.

Each FRU or Field Replaceable Unit within a 5000 chassis has in-built sensors designed to inform the Shelf manager of the health of the device. The Shelf Manager uses this information to monitor and take action, for example, generating a trap or log entry.


Solution

This example uses a FortiGate-5001A blade.  Each Fortinet blade has a number of sensors which capture the temperature, the voltage, and the hot-swap status. These sensors report to the Shelf Manager situations where the threshold values are exceeded so that appropriate action can be taken.

 Each sensor has 3 thresholds :

  • Upper Non-Critical Threshold
  • Upper Critical Threshold
  • Upper Non-Recoverable Threshold

 Each time the sensor exceeds a threshold a log entry will be created. 

If the Upper Critical Threshold is exceeded, a critical alarm will be generated in the log and the Critical Alarm light illuminated on the Shelf Alarm Panel.

To view the log and issue the example commands you must be in the Command Line Interpreter, this is achieved by logging into the Shelf Manager and typing CLIA.

 # clia

Pigeon Point Shelf Manager Command Line Interpreter

CLI>


 An example Log Entry is outlined below – this was obtained by viewing the log using the [clia sel] command.  .

 0x0018: Event: at Apr 27 17:45:19 2010; from:(0x98,0,0); sensor:(0x01,14); event:0x1(asserted): "Upper Non-Critical", 0x07 0xFF 0xFF

 To decode the  events in the log you can use the verbose command [clia sel –v] which provides additional information for each log entry.

0x0018: Event: at: Apr 27 17:45:19 2010; from IPM Controller: 0x98, LUN: 0, Channel: 0
    "Temperature" (0x01) sensor # 14
    "Threshold" (0x01) event Asserted
    "Upper Non-Critical Going High"

This log entry states that on [Fru = 98] the sensor [14] has reported exceeding the ‘’Upper Non-Critical’’ temperature threshold.

To further decode the event in the log, below are some example commands


1.  Confirm which FRU is generating the alarm by verifying the FRU information.

CLI> fru 98

98: FRU # 0
    Entity: (0xa0, 0x60)
    Hot Swap State: M4 (Active), Previous: M3 (Activation In Process), Last State Change Cause: Normal State Change (0x0)
    Device ID String: "FG5001A"

This highlights that the alarm has come from a temperature sensor on a FG5001A blade.


2.  Check the Sensor Threshold values

CLI>threshold 98 14

98: LUN: 0, Sensor # 14 ("DS75 Temp")
    Type: Threshold (0x01), "Temperature" (0x01)
        Upper Non-Critical Threshold, Raw Data: 0x32    Processed data: 50.000000 degrees C
        Upper Critical Threshold, Raw Data: 0x41    Processed data: 65.000000 degrees C
        Upper Non-Recoverable Threshold, Raw Data: 0x50    Processed data: 80.000000 degrees C

From this information we can determine that the Upper Non-Critical threshold has been exceeded, the threshold value is 50 degrees C.


3.  Now we check the current value of the Sensor

CLI>sensordata 98 14

98: LUN: 0, Sensor # 14 ("DS75 Temp")
    Type: Threshold (0x01), "Temperature" (0x01)
    Belongs to entity (0xc1, 0x61): FRU # 1 (AMC # 1)
    Status: 0xc0
        All event messages enabled from this sensor
        Sensor scanning enabled
        Initial update completed
    Raw data: 47 (0x2f)
    Processed data: 47.000000 degrees C
    Status: 0x00

This indicates at the time the sensor was verified it reported 47 degrees which is close to the threshold value.


Conclusion & Recommended Actions

To summarize the log entry indicates that a sensor on a Fortinet blade has reported to the Shelf Manager that it has exceeded a temperature threshold but not to a critical level.  It should be noted that the Shelf Manager constantly monitors temperature sensor information from all installed devices and will automatically raise and low the fan tray speeds to allow for dynamic cooling.  It may therefore be that no action is required in this situation.

Depending on the frequency, one follow-up action would be to verify the fan trays to see if they are all working correctly and producing optimal cooling.


Contributors